new slab 3inch vertical to 2nd floor is off center for 2 bath groups one on each side of a horziontal of tee can i run 2qty 45ells to straighten?

Users who are viewing this thread

boattm48

New Member
Messages
2
Reaction score
0
Points
1
Location
Suwanee Ga, Gwinnett county Ga
new house slab with 3 inch vertical stack for 2nd floor with tee horizontal branches for 2 bath groups one on each horizontal branch- I need to run two 45 ells on each horizontal branch about 5 ft each distance to vertical stack to straighten and align horizontal branch with the vertical stack off set. I read IPC chapter 7 and copilot wrote I could use 2 qty 45 ells in a horizontal branch- I sure hope so .Please advise
thanks boattm48
 

Jeff H Young

In the Trades
Messages
9,115
Reaction score
2,296
Points
113
Location
92346
dang another post no compredo? but generally yes 45s can be used on horrizontal waste lines
 

Tuttles Revenge

In the Trades
Messages
4,297
Reaction score
1,508
Points
113
We definitely need to know more about what the 2 horizontal drain lines are being used for and what configuration. Are they in a horizontal wet vent or just drains from separately vented fixtures?
 