POTTERTON PROMAX 33 COMBI Boiler Issue

Users who are viewing this thread

boiler101

New Member
Messages
2
Reaction score
0
Points
1
Location
London, England
Hello,

I have a Potterton Promax 33 Combi boiler - GC: 47-393-49 and having some issues.

I have changed the diverter valve, temperature sensor, and DHW filter. When I try to reset the boiler it doesn't seem to be doing anything, does anyone know how this can be checked or the selector switch how can that be checked to confirm if it is functioning correctly?

Note: There are no error codes appearing on the boiler

Many Thanks
 

Fitter30

Well-Known Member
Messages
4,421
Reaction score
817
Points
113
Location
Peace valley missouri
Here's their service manual. Look at page 55 - A. There are two fuses one is internal other is external. Page 53 a flow chart. Never heard of this brand manual is written different from the manufacturers from the states


This manual has a little easier wiring
 
Last edited:

boiler101

New Member
Messages
2
Reaction score
0
Points
1
Location
London, England
Thanks fitter30, fixed one issue but got following two:

1. When I turn the thermostat on, the boiler is igniting approx 2 mins after the demand for central heating. Any ideas what could be cause of this?
2. The DHW has been set to full heat now and still the temperature of the water is only luke-warm? What could be checked for this part?

I took off the plate heat exchanger and that doesn't look that dirty so abit weird. Diverter valve I changed as well 2 days back.
 