Basement Sink Plumbing

Users who are viewing this thread

elockwood

New Member
Messages
7
Reaction score
0
Points
1
Location
Washington State
Hello,

I am in the process of adding a kitchenette to our finished basement but have run into a challenge with the plumbing. The basement kitchen is directly below the main floor kitchen. I had hoped to use the existing drain line from the upstairs. However, this is only a 2 in drain and based on my understanding of the plumbing codes that apply here in WA State, this DFU is maxed out since it is draining both a sink and dishwasher from the upstairs. Which would mean there is not a code-compliant way to add a sink to this existing drain pipe.

My other option is to run a trap arm along the back wall and then over to the main drain. The challenge I see with this is the length of the trap arm, it would need to be ~25ft, the sink rough in drain height to maintain slope on the trap arm, and the need to vent the trap arm. I've attached a drawing of what I'm looking at.

Any thoughts on how best to approach this? Thanks

Ok thanks for the help,

I must have been doing a terrible job deciphering the DFU charts I was looking at. One other question if you don't mind, this is the drain from the sink/dishwasher on the main floor and it uses an AAV. Does this create an issue with having an AAV on a single drain on two floors? If not, what height does the basement sink AAV need to be (I've seen 6in above flood level)?
 

Attachments

  • plumbing.JPG
    plumbing.JPG
    36.9 KB · Views: 60
  • IMG_4424 (1).jpg
    IMG_4424 (1).jpg
    105.5 KB · Views: 58
Last edited:

Jeff H Young

In the Trades
Messages
9,109
Reaction score
2,292
Points
113
Location
92346
8dfu right ? 2 kitchen sinks whats the problem? the pic and drawing I dont quite get but you described a stack with a sink belw and another above 4 fixture units total
 

elockwood

New Member
Messages
7
Reaction score
0
Points
1
Location
Washington State
Thanks! Must have been doing a terrible job deciphering the DFU charts I was looking at. One other question if you don't mind, this is the drain from the sink/dishwasher on the main floor and it uses an AAV. Does this create an issue with having an AAV on a single drain on two floors? If not, what height does the basement sink AAV need to be (I've seen 6in above flood level)?
 

Attachments

  • IMG_4424 (1).jpg
    IMG_4424 (1).jpg
    105.5 KB · Views: 60

elockwood

New Member
Messages
7
Reaction score
0
Points
1
Location
Washington State
8dfu right ? 2 kitchen sinks whats the problem? the pic and drawing I dont quite get but you described a stack with a sink belw and another above 4 fixture units total
Thanks, added a photo of the drain from the upstairs. It uses an AAV, I'm struggling to understand the code for if/how to connect the basement sink property with AAV on two floors on a single vertical drain.
 

elockwood

New Member
Messages
7
Reaction score
0
Points
1
Location
Washington State
A vertical 2 inch pipe? That can take 16dfu.

A dishwasher doesn't add to the dfu's.
Thanks, added a photo of the drain from the upstairs. It uses an AAV, I'm struggling to understand the code for if/how to connect the basement sink property with AAV on two floors on a single vertical drain.
 